NFPA 664 - Wood Processing & wood working facilities 1
MechGuy22
Hello everyone. I wanted to get some opinions on this. We have a wood working/metal working shop that is part of a much larger building. The total shop area is about 1600 ft^2.
According to NFPA 664 chapter 1, standard 664 only applies to shops over 5,000 ft^2. Does this mean that if the shop is less then 5000 ft^2 a dust collection system is not required at all? Or is this just saying that it doesen't have to comply with NFPA 664 if it is less than 5000 ft^2?
Thanks everyone.
NFPA 664 applies to your building because its area is greater than 5,000 square feet. NFPA 664 is concerned with the accumulation of wood flour over a building area larger than 5,000 square feet. If your client can't control the hazard, then the potential for a dust explosion could possibly be created by your client.
You may read about this hazard in an article I wrote several years ago and I attached to this message. Good luck.
 http://files.engineering.com/getfile.aspx?folder=294156de-5847-4683-b1f1-38af499f27eb&file=dust_deflagrations.pdf
Thank you for your reply, as well as the uploaded file.