NFPA 219 flow testing hydrants, 25% drop
davidfire
Industrial
GB
[smile]Hi,
Im trying to comply with the 25% drop in residual\static specified in NFPA 219 when carrying out hydrant flow testing. example below
Remote static 158 psi
hydrant 1 open with residual 154psi and flow 2627 lpm
hydrant 2 open with residual 140psi and total flow (x2 hyds)4735 lpm
hydrant 3 open with residual 116psi and total flow (x3 hyds)6545 lpm
total flow 6545 x (158-20)0.54 / (158-116)0.54 = 6545 x 138 0.54/42 0.54 = 9320 lpm Is this correct?
also
if I had a fire pump with a gauge that showed 170psi and the pump gauge drops whilst opening the hydrants, should I include this in my theoretical calc? if so how?
Thanks for any help
me again!! sorry my theoretical calc should've said 12442 lpm.
Sorry have not done a flow test with a fire pump
On the line and do not know if it is figured in
I think you may have a good representation of the water supply
4.3.6 To obtain satisfactory test results of theoretical calculation of expected flows or rated capacities, sufficient discharge should be achieved to cause a drop in pressure at the residual hydrant of at least 25 percent, or to flow the total demand necessary for fire-fighting purposes.
""" to flow the total demand necessary for fire-fighting purposes"""""
what is your demand you need??
The area is a storage tank farm so the demand for fighting purposes will easily be exceeded and additional water supplies required!
The way that I am viewing your numbers is that you have a total of 6545 lpm at a residual pressure of 116 psig taken at the remote static point which I assume is a fourth hydrant; Hydrant flows at 2108 lpm and hydrant 3 flows at 1810 lpm. So plot the remote static value of 158psig and the 6545 lpm at 116 psig on semi-log graph of N=1.85 power to see what lpm at 20 psig the graph shows. I have included an attachment of the graph in question with your values. At 20 psig, 3270 gpm translates to 12376.9 lpm and 3540 gpm translates to 13398.9 lpm.
 http://files.engineering.com/getfile.aspx?folder=5585b9fb-07ac-45a1-9597-3acd3a5c7e8c&file=Reply_to_thread_184-344545.pdf
That s/b "...Hydrant 2 flows at 2108 lpm and hydrant 3 ......"
NFPA 291 Recommended Practise for Fire Flow Testing and Marking of Hydrants
Slip of the typing finger, it would appear.