Would it be possible to size the pessure tank for the sprinkler duration and domestic needs?
not a designer, and not sure of the question, but if one is can you use the same tank for domestic use and sprinkler use???
my question would be how do you know at any given point that there is enough water in the tank to meet the sprinkler requirement???
6.1.2 Where stored water is used as the sole source of supply, the minimum quantity shall equal the water demand rate times 10 minutes unless permitted otherwise by 6.1.3.
6.1.3 Where stored water is used as the sole source of supply, the minimum quantity shall be permitted to equal the two-sprinkler water demand rate times 7 minutes where dwelling units meet the following criteria:
(1) One story in height
(2) Less than 2000 ft2 (186 m2) in area
6.2* Water Supply Sources.
The following water supply sources shall be considered to be acceptable by this standard:
(1) A connection to a reliable waterworks system with or without an automatically operated pump
(2) An elevated tank
(3) A pressure tank designed to American Society of Mechanical Engineers (ASME) standards for a pressure vessel with a reliable pressure source
(4) A stored water source with an automatically operated pump
(5) A well with a pump of sufficient capacity and pressure to meet the sprinkler system demand. The stored water requirement of 6.1.2 or 6.1.3 shall be permitted to be a combination of the water in the well (including the refill rate) plus the water in the holding tank if such tank can supply the sprinkler system.
6.2.1* Prior to system acceptance, a system utilizing a pump shall be tested by opening the drain/test connection. The pump shall sense the flow, turn on, and flow water for the required duration of 6.1.2 or 6.1.3 (as appropriate) without interruption.