As others have said you need to get someone who is knowledgeable in sprinkler design to come out and look at your building. NFPA 13 has requirements based on what you store, how you store it, etc , etc. For example metal on a wood pallet, stored on double row racks, 8' aisle, requires a density of .29, but for cardboard boxes on wood pallets, same storage configuration requires a density of .37. Same product stored closer together say a 4' aisle is now .33 and.43 respectively. So many variables to consider.
Good luck.
****************************************