The initial comment passed around:
"Site does not appear to have available city water and we will have to use the existing well for Domestic Water. As far as Fire Protection is concerned, there will be a need for a Fire Pump as well as a water Storage tank.
The storage tank needed for this building will have to be quite large and located somewhere near to the Fire Pump building. Initially, the storage tank should be filled via outside water source with a water feed from the domestic line controlled by a float switch will add water as necessary to maintain a minum level for fire protection.
I will need to know the hazard level of the building to estimate the storage tank size. If light hazard, the water demand will be Hose Stream Demand (100 gallons per minute for 30 minutes per NFPA 13 Table 5-2.3) plus the water supply for sprinklers ( .10 gallons per minute/square foot for 30 minutes). If a higher Hazard is considered, the water demand for the Fire Sprinkler System can be much higher than this.
From some quick calculations that I have come up with, we could be looking @ a 70,000-140,000 gallon tank depending on the Hazard level of the spaces. Remember, the tank has to hold enough water to allow the water flow @ a minimum gpm for 30-60 minutes depending on the Hazard level."
Reply to the above:
"The assessment indicated below is correct to the extent that a fire pump and storage tank are required if the building is sprinklered and the city water supply is not adequate to meet the demand. However, I question the tank size indicated in this email. I am assuming this is a car dealership with a service facility. The showroom would fall into an Ordinary Hazard, Group 1 occupancy while the repair shop would be Ordinary Hazard, Group 2. The hose stream demand and required duration of supply is the same for both classifications. For Ordinary, 2, the required density and area are .2 gpm/sq ft over a design area of 1,500 sq ft. This will require a flow rate of 300 gpm. The hose stream requirement is 250 gpm. The required duration for this occupancy ranges from 60 to 90 minutes. Taking worst case scenario you will be flowing 300+ 250 = 550 gpm for 90 minutes. Throw in 15% additional flow for safety and this would be 630 gpm. Flowing 630 gpm for 90 minutes requires a total of 56,700 gallons.
I think the authority having jurisdiction may allow a smaller tank. The clients insurance company may also have a say in this as well, therefore the AHJ and insurance carrier should be consulted."
Reading the NFPA 13 is confusing on this issue... we are lacking experience with this as we rarely do fire protection design.
Thanks in advance -
~MX
Reply to the above:
Thanks in advance -