I copied and pasted your doc file below:
-----------------
I have some questions regarding the below fire pump sprinkler installation and testing requirements. The fire pump in question is a marine application.
1.Firstly, is it not true, that to ensure my pump is able to perform at 150% at no less than 65% of the rated head pressure I will need the TDH rating of the pump? I have looked for standard specifications of several centrifugal pumps on-line and this particular pump nameplate, the rated head is not listed on either. Is the max head pressure determined following the delivery performance curve calculations? Or it a specification I should have. I am trying to make sense of a recent service report indicating my installation was not able to perform at 150%. With no mention of the TDH, I don’t think that statement can be deduced accurately. One issue is that NFPA 25 (inspection) does not elaborate the “at no less than 65% max head” requirement, NFPA 20 (pump requirements) does.
2.NFPA 25, 8.3.3.2 requires the pump run at the no-flow condition (churn) for ½ hour. Is the purpose of this to ensure the pump does not overheat? Or, to test the circulating relieve valve, I see the circulating relive valve is required yet I fail to
------------------
In order for a fire pump to be listed it must produce 150% of its rated capacity at 65% of its rated pressure. If it is red and has a UL and/or FM sticker on it the pump will give that performance at a minimum and, most likely, more.
Sounds like the pumps you are looking at are not listed fire pumps?
Not sure about NFPA #25 but I think it is both.