SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,264
I have a 40,000 sq ft warehouse for a rack storage of non-expanded Group A plastic most of which is cartoned but there is some that is exposed. I didn't take count but would estimate 20% to 30% is exposed.
Building measures 200'x200' having 25' bays and your typical bent metal purlin construction.
Eave is 19'-8 1/2", roof has 1 in 12 pitch which puts peak at exactly 28'-0 1'2" AFF.
Existing system designed 30 years ago for .17/2,000 using public water. Line from the city is 103' of 6" cement lined ductile iron. Riser is in the corner of the building.
Just ran a flow test this morning and obtained:
Static 62 psi
Residual 45 psi
Flow 1,163 gpm
For full flavor see photo below:
The recommendation letter from the insurance company reads "Plastics warehouses; at least of of the areas has a ceiling height of 22' and for rack storage 15' high in an area with a 22' ceiling NFPA 13 Chapter 17 Figure 17.2.1.2.1(b) requires either 1 level of in-racks with a ceiling density of .3/2000 or a ceiling density alone without in-racks of .6/2000."
The .6/2000 is clearly out but I can barely make it with .3/2000 with one row of 1/2" in rack sprinklers discharging at 15 psi minimum. By barely make it I have a pretty large grid and I am stuck with a 3 psi safety factor.
But given the clearance (13') I don't see where this is appropriate.
I am fairly new to using both the 2010 and 2013 editions of the standard so am I missing something here?
Building measures 200'x200' having 25' bays and your typical bent metal purlin construction.
Eave is 19'-8 1/2", roof has 1 in 12 pitch which puts peak at exactly 28'-0 1'2" AFF.
Existing system designed 30 years ago for .17/2,000 using public water. Line from the city is 103' of 6" cement lined ductile iron. Riser is in the corner of the building.
Just ran a flow test this morning and obtained:
Static 62 psi
Residual 45 psi
Flow 1,163 gpm
For full flavor see photo below:

The recommendation letter from the insurance company reads "Plastics warehouses; at least of of the areas has a ceiling height of 22' and for rack storage 15' high in an area with a 22' ceiling NFPA 13 Chapter 17 Figure 17.2.1.2.1(b) requires either 1 level of in-racks with a ceiling density of .3/2000 or a ceiling density alone without in-racks of .6/2000."
The .6/2000 is clearly out but I can barely make it with .3/2000 with one row of 1/2" in rack sprinklers discharging at 15 psi minimum. By barely make it I have a pretty large grid and I am stuck with a 3 psi safety factor.
But given the clearance (13') I don't see where this is appropriate.
I am fairly new to using both the 2010 and 2013 editions of the standard so am I missing something here?