ContractorDave
Mechanical
- Jan 16, 2007
- 364
We are overseeing a tank farm project where a low expansion foam system is being installed to NFPA 11. There are (4) tanks with (7) 550gpm chambers a piece. The system is calling for 4000 gpm@ approx. 120 psi which will mean in this case (2) 210 hp electric pumps. The design is to be fully manual. So here’s a twist thrown by NFPA 11: In Ch4 under 4.2 Water Supplies; 4.2.2 Water and Foam Concentrate Pumps;
4.2.2.1 When water or foam concentrate pumps are required for automatic foam system operation, they shall be designed and installed in accordance with NFPA 20.
4.2.2.2 Controllers in accordance with NFPA 20 shall not be required for manual systems.
Question A to 4.2.2.1: What if they are NOT automatic?
Question B to 4.2.2.2: I assume the controllers still have to be listed… just not designed or installed as per NFPA 20? What would be the guidelines then?
Sorry about the long winded explanation / question.
4.2.2.1 When water or foam concentrate pumps are required for automatic foam system operation, they shall be designed and installed in accordance with NFPA 20.
4.2.2.2 Controllers in accordance with NFPA 20 shall not be required for manual systems.
Question A to 4.2.2.1: What if they are NOT automatic?
Question B to 4.2.2.2: I assume the controllers still have to be listed… just not designed or installed as per NFPA 20? What would be the guidelines then?
Sorry about the long winded explanation / question.