38.3.2.1 General. Hazardous areas including, but not limited to, areas used for [highlight #FCE94F]general storage[/highlight], boiler or furnace rooms, and maintenance shops that include woodworking and painting areas shall be protected in accordance with Section 8.7.
My opinion is that the "general storage" wording above says you need to protect it, and is what drives you to 8.7. But it depends on the AHJ. How much paper, a couple of boxes, or a couple of pallets? And is it a supply closet, or a storage room? Compact mobile shelving? All of these factor in. I'd ask your AHJs (fire dept, building inspection dept, and insurance carrier, et al).
Stookeyfpe, this is where I got the smoke partition requirement, based on a "new" occupancy:
8.7.1.2 In new construction,[highlight #FCE94F] where protection is provided with automatic extinguishing systems without fire-resistive separation, the space protected shall be enclosed with smoke partitions in accordance with Section 8.4[/highlight], unless otherwise permitted by one of the following conditions:
(1) Where mercantile occupancy general storage areas and stockrooms are protected by automatic sprinklers in accordance with Section 9.7
(2) Where hazardous areas in industrial occupancies are protected by automatic extinguishing systems in accordance with 40.3.2
(3) Where hazardous areas in detention and correctional occupancies are protected by automatic sprinklers in accordance with 22.3.2