NEUTRLA GROUNDING RESISTOR PERMANENT CURRENT 1

Status
Not open for further replies.

tszpun

Industrial
Oct 22, 2013
28
Hello Experts,

We are specifying Neutral Grounding Resistor for our industrial distribution system.
We already know the fault current level, which is 1000 amp for 5 sec.
However, I do not know how to specify the permanent current value.
Does any body know, how I can find / calculate the permanent current value for neutral grounding resistors ?

Regards,
tszpun
 
Replies continue below

Recommended for you

It depends.

If all you feed are high-side delta windings it will be pretty darned low. If you feed wye-wye transformers with single phase loads it could be most anything. Nobody here can come up with a better number than you can.

I’ll see your silver lining and raise you two black clouds. - Protection Operations
 
Per IEEE 32, there is no continuous rating assigned for neutral grounding resistors.
In case of Inductive devices (neutral grounding transformers etc.), a 10s rated device will have continuous rating of 3% (of 10s rating).
Since there is no 5s rating mentioned in the standard, we may use the same 3% formula.