a10jp
Electrical
- May 18, 2005
- 150
When you have parallel generator (emergency standby, permament installation) in operations, through a set of parallel switchgear, is there any special consideration that requires the ATS to also switch the neutral? In the case of a single emergency generator, I always prefer to solidly bond the generator neutral to neutral bus at the main dist panel, which is grounded at that point. In that case I can use a 3-pole transfer switch. But for parallel generator operation, is there something else to consider?