Remember, a generator is FEEDING power to various loads, the distribution of which is not in the purview of the generator mfr. resulting in the possibility that the generator must be capable of feeding an unbalanced load.
In the same machine used as a MOTOR, the only load is the motor windings themselves. So how is the load current going to be unbalance if it is not a problem leading to shut down? In other words, you don't WANT a motor running continuously in an unbalanced condition, so there is no need to ground the eye point anyway.