Hi,
If I have a utility transformer, lets say 13.8 kv/0.6V DY1n, 2MVA, with the neutral grounded at the MV/LV utility substation ground grid, and then I am going to distribute the energy with a 4 wire cable (3ph + neutral)and connect the neutral to ground at every main service point with a grounding electrode.
Correct me if I am wrong but it seems to me that the substation ground grid and the electrodes at each service point are then all connected through the neutral wire.
What happens in case there is a fault at the MV size of the substation? Then all the ground grid at the substation and the electrode system at the service point will be rise to GPR that can be more than the 600 V of a LV system. Does this mean that the electrode systems at every service point need to comply with the IEEE 80 requirements for step and touch voltage?
Why then the NEC recommend this practice (250.24)? Shouldn't we isolate the neutral from the substation ground grid and connected only to the service point electrodes?
Thanks.
If I have a utility transformer, lets say 13.8 kv/0.6V DY1n, 2MVA, with the neutral grounded at the MV/LV utility substation ground grid, and then I am going to distribute the energy with a 4 wire cable (3ph + neutral)and connect the neutral to ground at every main service point with a grounding electrode.
Correct me if I am wrong but it seems to me that the substation ground grid and the electrodes at each service point are then all connected through the neutral wire.
What happens in case there is a fault at the MV size of the substation? Then all the ground grid at the substation and the electrode system at the service point will be rise to GPR that can be more than the 600 V of a LV system. Does this mean that the electrode systems at every service point need to comply with the IEEE 80 requirements for step and touch voltage?
Why then the NEC recommend this practice (250.24)? Shouldn't we isolate the neutral from the substation ground grid and connected only to the service point electrodes?
Thanks.