Suggestion: There are various neutrals in power distribution systems. E.g. there is a transformer neutral, generator neutral, motor neutral, system voltage neutral.
The system voltage neutral is the one that can have the current as high as the conductor ampacity rating permits. In some voltage systems, it is actually doubled.
The transformer/generator neutral current strongly depends on the number of wire of the power distribution system. E.g. if you have three-phase four-wire system, i.e. three-phase plus neutral, then the neutral current can increase up to neutral conductor ampacity rating.
However, if you have a three-phase three-wire system, then the neutral current is usually limited by some system grounding method protective scheme at transformer/generator, e.g. high resistance grounding, etc. In this case, the transformer/generator neutral current can be limited to 5A or 10A depending on the system grounding design.
So, all what is needed is to make certain that the neutral is interpreted and treated correctly, and relevant current values are being considered.