In the UK the electromechanical distance relays will trip the circuit for a blown fuse, instead of locking up. In some other European countries there's a different approach and the protection will lock up for blown VT fuse, hence relying on the protection ‘to know’ if it's a genuine fault or not. In the UK, having a stiff system they decided to trip regardless, for the same reason they don't lock up the protection for power system swings, deemed unlikely to happen.
So, if you have a circuit trip and distance protection operated at one end only, also VT supervision alarm up (blown fuse), you can work out it was a malop