In his 9/3 post, SMB1 wrote:
any LG fault in Y side will behave as LL fault in the Delta side.
The fault current will flow on one winding (Y side). After applying the (AmpsXTurns) concept the current in the Delta side will flow also on one winding.
So, in the (HV)Delta side during the LG fault in(LV)Y side
The fallacy is in treating sequence currents like fault currents. Even though, during a low side line-to-ground fault, there is fault current in only one low side phase and two high side phases, there is negative sequence current in all three phases of both the low side and the high side. The positive and negative sequence currents are present in all three phases and are equal.
If you had 4500A <0° in secondary Phase A, then on the secondary side:
Voltage ratio=69000/13800=5
Turns ratio=8.66
Ia0=Ia1=Ia2=1500<0°
Ia=4500<0°, Ib=0, Ic=0
on the primary side:
IAC=519.6<0°, IBA=0, ICB=0
IA=IAC-IBA=519.6<0°, IB=IBA-ICB=0, IC=ICB-IAC=519.6<180°
IA0=0, IA1=300<30°, IA2=300<-30°
IA1 and IA2 both flow in Phase B, but from the definition of symmetrical components:
IB=IA0+a²·IA1+a·IA2 where a=1<120°, a²=1<240°
IB=0+300<270°+300<90°
IB=0