Tripping out should not cause an imbalance problem. If no phase history then try to start one. If level increases to .7 ips then I would recommend inspecting motor, coupling, and driven unit. What is unit driving and what are levels on the driven unit. Had a call out on a vertical motor one time due to high vibrations. It was driving a pump they had not taken readings on. The bearings in the pump were trashed. Problem solved with repairs.