I have a 120 VDC brushed motor that we have been switching on and off using an Omron G2RL-24-DC12 relay (contacts rated at 8A 250VAC, 8A 30 VDC). The relay contacts have been "sticking" occasionally, presumably from arcing as a result of switching an inductive load. The motor is being driven by unfiltered, unregulated 120VDC which is obtained by rectifying the 120VAC line with a full-wave bridge. There is a 0.47uF suppression cap across the motor terminals along with an MOV for surge suppression. The motor draws about 2 amps when running normally, but its current could rise to 4-5 amps when it is laboring (and possibly higher when it is first switched on, but no measurement on that yet).
Would a solid state switching scheme be appropriate here? Perhaps replace the mechanical relay with an SCR or Triac?
We do not need to control the motor speed, just on and off. The direction is controlled by another DPDT relay that flips the polarity of the motor excitation voltage. This relay, however, is not sticking because it is never energized/de-energized with power on its contacts.
A microcontroller output is presently driving a transistor that switches the G2RL-24-DC12 coil voltage on/off. So the solution will require interface to a microcontroller output pin...
Thanks for your input.
Mike
Mike