Dear Mr. cherryg (Electrical)(OP)19 Jul 22 18:51
"...#1. .... I don't have the Code book, .... I believe that NEC requires the equipment grounding conductor for resistance grounded systems also. #2. What is the rationale behind this?? eg. for a LV system with 10A resistor, we would only be detecting GF current using CBCTs and only for detection, with no intentional tripping. #3. In that event, why would we need a low impedance path for the fault current using a PE conductor? Even fault in milliamps can be detected using a CBCT and GF relay on each LV feeder..."
#0. Usually for LV installation works, the " Code " book refers to the NEC in US. Whereas PE conductor is an IEC terminology; which does NOT appear in the NEC.
#1. Yes. See NEC 250-36 titled High-impedance grounded neutral systems for detail.
#2. The equipment including enclosure is connected by PE conductor to the Ground bar. A bonding jumper conductor connects the Ground bar to the grounded side of the grounding impedance..
#3. The purpose is to ensure at all times that the equipment including enclosure is maintained at Ground (in US) or Earth (in IEC) potential; safe to touch.
Che Kuan Yau (Singapore)