Durdy

Chemical
Sep 14, 2007
1
Gents,

Here is the deal, I have Flow meter FHKU 100 installed on disinfection system. The flow meter have +8V, GND and IN connections on control panel, and displays flow rate on control panel.
I need an analog input (+,-) to the system to control the disinfection rate 0-20 mA or 4-20 mA. It will be perfect if i can get this signal from flow meter proportional to flow rate, meaning maximum flow 20 mA, no flow 0 or 4 mA.
Is there any way to convert or get parallel signal from this flow meter.
thnx in advance.
cheerz
 
Replies continue below

Recommended for you

According to web specs for the FHKU 100, it has an open collector, pulse output, with the somewhat odd pulse rate of "approx. 65 Imp./ l (Nozzle 10mm)" [im]pulses per liter?


So, in answer to your question, if your controller needs an analog signal, you might consider
a) getting a flowmeter that outputs flow rate directly as an analog signal.
b) converting the open collector pulses to an analog flow rate signal with a frequency converter, a pulse-to-analog converter

Devices like the Precision Digital PD693 panel meter takes an open collector input, displays the flow rate and with an optional analog output provides an isolated 4-20mA flow rate signal.

Or the Phoenix Contact MCR-f-UI-DC, 2814605 is a DIN rail mount frequency converter, but it requires a software programming kit and cable to scale the output.


Or there are a hundred other I/O manufacturers' frequency converters that will do the job.

Dan
 