Need a ONS in a SLC 5/03 1

Status
Not open for further replies.

eric34

Electrical
Joined
Feb 17, 2007
Messages
22
Location
CA
I am use to using PLC 5 or control logix and I need a one shot instrution in the old slc,it doesn't seem to support it.Is there something in the S2 file I can use?
 
The SLC 5/03 supports the OSR inststruction which can be set up to do equivelent ONS by setting up the input conditions correctly. Of course, 2 bits are required, one as inline condition and one for the OTE. The OTE address becomes the one-shot bit in subsequent logic, the other is simply to inform the processor of the status of the OTE as the "one-scan on" address.
 