Does this extract help?
FIELD TESTING
6.1 PURPOSE
The purpose of field testing is to:
(a) reveal the occurrence of faults in the laying procedure, e.g. joints incorrectly installed or pipes damaged;
(b) reveal the occurrence of faults in the assembly procedure of pipeline components, e.g. tapping bands, maintenance structures, frames and covers;
(c) in the case of pressure pipelines, determine that the pipeline will sustain a pressure greater than its design pressure without leakage;
(d) in the case of non-pressure pipelines, determine that the pipeline satisfies the requirements for infiltration and exfiltration; and
(e) test the installed structural integrity of the pipeline;
Field testing is not intended to supplement or replace the test requirements of product Standards.
6.2 PRESSURE PIPELINES - HYDROSTATIC PRESSURE TESTING
6.2.1 General
The hydrostatic pressure test method shall be as specified.
Hydrostatic pressure testing requires selecting an appropriate configuration of method, pressure and length of test section.
Test parameters and details shall be determined with due consideration to the following:
(a) pipe material;
(b) pipe diameter
(c) length of test section;
(d) magnitude of test pressure, rate of pressurisation and duration of the test;
(e) presence of air in the pipeline;
(f) time required for saturation of porous liners;
(g) potential movement of pipeline thrust restraints;
(h) design pressure for thrust and anchor supports;
(i) accuracy of test equipment;
(j) ambient temperature changes during testing;
(k) presence of leaks in equipment used for testing or equipment attachment points (e.g. sealing plugs); and
(l) potential for leaks in the pipeline.
NOTE: It is advisable to begin testing early in the pipeline installation to confirm adequacy of laying procedures, and where appropriate, to increase the length tested progressively as experience is gained.
6.2.2 Selection of test pressure
The hydrostatic test pressure at any point in the pipeline shall be:
(a) Not less than the design pressure;
(b) Not more than 25% above the rated pressure of any pipeline component.
NOTE: The design pressure includes the short term surge pressure (water hammer) as determined by analysis (see Clause 1.4.8).
Compressed air testing shall be carried out in accordance with Clause 6.4.2.
NOTE: Air test pressures in excess of 50 kPa should not be applied due to safety considerations.
6.2.3 Selecting test lengths
The pipeline length tested shall be either the whole, or a section (capable of being isolated), of the pipeline depending on the length and diameter, the availability of water and the spacing between sectioning valves or blank ends.
The pipeline shall be divided into test sections such that:
(a) The hydrostatic test pressure at any point in the pipeline is —
(i) Not less than the design pressure;
(ii) Not more than 25% above the rated pressure of any pipeline component.
(b) Water is available for the test together with facilities for its disposal, in accordance with regulatory requirements, after the test.
NOTES:
1 Pipelines longer than 1000 m may need to be tested in several sections. Where long lengths are to be tested, radio or other electronic means of communication between test operatives, to coordinate test procedures and thus minimise the test duration, is desirable.
2 Long test sections may incorporate a large number of mechanical (i.e. flanged) joints, which should be checked for leakage. The longer the test section the harder it is to locate a leak, or discriminate between a leak and the other effects, such as the absorption of air into solution under pressure.
6.2.4 Pressure test methods
6.2.4.1 Constant pressure (water loss) method
The test length shall be hydrostatically pressure tested in accordance with Appendix M, Paragraph M4.
NOTE: This method is suitable to DI, GRP, PVC, and steel pipelines.
The test length shall be acceptable where:
(a) there is no failure of any thrust block, pipe, fitting, joint or any other pipeline component;
(b) there is no visible leakage; and
(c) The quantity of make-up water necessary to maintain the test pressure shall comply with the following Equation:
. . . 6(1)
where,
Q = allowable make-up water, in litres per hour
D = nominal diameter of the test length, in metres
L = length of the test length, in kilometres
H = average test head over length of pipeline under test, in metres
NOTE: The make-up water is not a leakage allowance, but is an allowance to cover the effects of the test head forcing small quantities of entrapped air into solution. Normally the test should last for a minimum of 2 h and be concluded within 5 h to 8 h. The make up water requirement should reduce with time as air goes into solution. Where, after 12 h the make up water still exceeds the allowable limit, testing should cease and the cause of loss investigated.
6.2.4.2 Constant pressure (water loss) method for visco-elastic pressure pipelines
The test length shall be hydrostatically pressure tested in accordance with Appendix M, Paragraph M5.
NOTES:
1 This method is suitable for PE, PP and ABS pipelines.
2 Visco-elastic materials exhibit significant creep and hence the method given in Clause 6.3.4.1 is not appropriate.
3 This method is based on VAV P78.
The test length shall be acceptable where—
(c) the allowable make-up water, used to maintain the test pressure, shall be less than the quantity calculated from Equation 6(1).
6.2.4.3 Pressure decay method for visco-elastic pipelines
The test length shall be hydrostatically tested in accordance with Appendix M, Paragraph M6.
NOTES:
1 This method has been validated for PE pipelines, however, it may be used for other materials given appropriate test data.
2 Visco-elastic materials exhibit significant creep and hence the method given in Clause 6.3.4.1 is inappropriate.
3 This method is based on - Section 5 of 'A guide to testing of water supply pipelines and sewer rising mains', 1st Edition, June 1999, published by Water Research Committee (WRc Plc), UK.
(c) it passes the criteria of Appendix M, Paragraph M6.
NOTES:
1 When the test pressure is applied to a leak-free test section, there may be a reduction in pressure (pressure decay) in a non-linear manner, due to the creep response and stress relaxation of the material (see Figure 6.1(a)). Where the pressure decay is plotted against a logarithm of time, the result is expected to be a straight line (see Figure 6.1(b), line A-B). An increase in the slope of the line will indicate that there is leakage in the test section. A change to a steeper slope, as shown by line A-C, indicates the possibility of leakage.
2 Using the decay profile, the effect of leakage can be predicted by amending the calculation to take account of the drop in pressure due to the leak itself. The presence of any air trapped in the pipeline will also effect the shape of the line, since air is compressible and it will act to maintain the pressure over time. This will initially give a false reading. Line A-D, with an initial flatter slope, indicates air was present at the start of the test. The pressure loss method of Appendix M, Paragraph M5 gives guidance on the interpretation of different values for the slope of the line.
FIGURE 6.1 TYPICAL PRESSURE DECAY GRAPHS FOR PE PIPELINES
6.2.4.4 Pressure rebound method for visco-elastic pressure pipelines
The test length shall be hydrostatically tested in accordance with Appendix M, Paragraph M7.
NOTES:
1 This method is suitable for ABS, PE and PP pipelines, where a short test time is required.
Test pressures shall not exceed the operating pressure times any design or service factor for the material. Compressed air testing shall not be permitted for pressure pipe.
The test length shall be acceptable if—
(c) it complies with the criteria of Appendix M, Paragraph M7.
6.2.4.5 Visual test method for minor pipelines
The test length shall be hydrostatically pressure tested in accordance with Appendix M, Paragraph M8.
NOTE: This test may be appropriate for small installations of all materials, which are easily inspected visually for leaks.
(c) there is no pressure loss indicative of a leak.
6.2.4.6 Other test methods
NOTE: Testing may also be carried out in accordance with the material specific hydrostatic test methods of AS 2032, AS 2033 and AS 3690, for PVC, PE and ABS pressure pipelines, respectively.
6.3 NON-PRESSURE PIPELINES - LEAKAGE TESTING
6.3.1 General
Leakage testing is used to reveal locations of potential infiltration and exfiltration due to the inclusion of damaged pipes, seals or incorrectly made joints in the pipeline at the completion of installation.
Leakage testing for acceptance of non-pressure pipelines, shall be carried out by at least one of the following methods:
(a) low pressure air testing;
(b) vacuum testing;
(c) hydrostatic testing; and
(d) infiltration testing.
Leakage testing is not required for stormwater drains.
NOTE: Air and vacuum tests provide qualitative data only, as air pressure losses cannot be related directly to water leakage rates.
For pipeline test sections installed below the water table, and for submarine pipelines, the test pressure used for the hydrostatic test, and for the air test, shall be increased to maintain the required differential between internal and external pressure.
A pipeline failing to meet the requirements of the air or vacuum tests may be retested using the hydrostatic test method.
Failure is still probable.
6.3.2 Low pressure air test
The pipeline shall be tested in accordance with Appendix N, Paragraph N2.
The test length shall be acceptable where the gauged pressure exceeds 18 kPa (or 7 kPa less than at the pressure at the start of the test) for the time interval shown in Table 6.1 after the shut-off of the air supply.
This table is based on an air test pressure of 25 kPa (in excess of any external hydrostatic pressure due to groundwater) and, on this basis, air volume losses shall not exceed the greater of:
(a) a rate of 0.0009 m3/(minute ´ m2) of pipe wall area; and
(b) a rate of 0.056 m3/minute which is regarded as the lowest detectable individual air leak.
Column 2 and column 3 of Table 6.1 give the times and lengths up to which (b) prevails over (a).
6.3.3 Vacuum Test
The pipeline shall be tested in accordance with Appendix N, Paragraph N3.
The test length shall be acceptable where the vacuum does not decrease in magnitude below (-)18 kPa (that is a maximum drop in vacuum of 7 kPa) over the time interval shown in Table 6.1.
6.3.4 Hydrostatic test
The pipeline shall be tested in accordance with Appendix N, Paragraph N4.
The test length shall be acceptable, where the specified allowable make up water is not exceeded. Where not specified, the allowable make up water shall be 0.5 litres per hour per metre length per metre diameter.
6.3.5 Infiltration Test
The pipeline shall be tested in accordance with Appendix N, Paragraph N5.
The test length shall be acceptable where there is no infiltration over a 24 hour period.
NOTE: Where a free-standing water table is present at a level of at least 1.5 m above the test section, and 150 mm above any sideline connections, the absence of infiltration can eliminate the need for any of the previous tests.
An allowance for infiltration may be acceptable subject to approval.
TABLE 6.1
LOW PRESSURE AIR AND VACUUM TESTS—MINIMUM TIME INTERVALS FOR 7 KPA PRESSURE CHANGE IN PIPELINE
DN Minimum time(minutes) Maximum length for minimum time to apply(metres) Test length (metres)
50 100 150 200 250
Minimum test duration (minutes)
80100150 1.523 231185123 1.523 1.523 1.523 1.525 1.636
225300375 467 826249 467 5914 81422 101829 132336
450525600 91011 413531 101418 212837 314255 415673 527092
675750900 131417 272521 232941 465783 7086124 93115165 116143207
100010501200 192023 1918.815 515673 102112147 153169220 204225294 255281367
1500 28 12 115 230 344 459 574
NOTES: 1 The time interval may be reduced for a proportionate reduction in the allowable pressure drop. Where there is no detectable change in pressure after 1 hour of testing, the section under test shall be deemed acceptable.2 This table is based on the following equation: where,T = time for a 7 kPa pressure drop (seconds);Di = pipeline internal diameter ( metres);q = allowable volume loss in cubic metre/minute/ square metre taken as 0.0009 m3/min.m2 in Table 5.2;k = 0.054DL but not less than 1; andL = length of test section (metres).3 Columns 2 and 3 have been calculated with k=1.0.4 The appropriate air or vacuum test/ pressure method for pipes larger than DN 750 should be established by reference to the specifier.
6.4 DEFLECTION TESTING
6.4.1 General
For non pressure pipelines, and where structural verification for pressure pipelines is required, deflection shall comply with the test criteria of Table 5.6.
The allowable short term deflections of Table 5.6 are based on 30 day time intervals after embedment (and fill) placement and compaction. Where measurements are made over an alternative time interval, the allowable deflections shall be determined by multiplying the values in Table 5.6 by the appropriate time factor given in Table 6.2.
NOTE: Deflection measurement is a valuable method of assessing the adequacy of embedment material placement and compaction. Testing may be carried out as soon as practicable after completion of placement and compaction of all fill material over the pipeline.
TABLE 6.2
TIME FACTORS FOR DEFLECTIONS
(to adjust allowable 30 day deflections given in Table 5.6)
Time interval Factor
24 hours3 days7 days 0.700.750.85
14 days30 days3 months 0.951.01.1
1 year2 years 1.21.3
NOTE: Factor values may be interpolated for intervening time periods between 24 hours and 2 years. E.g. for 10 days=0.85+((0.95-0.85)´3/7)=0.89
6.4.2 Pipelines - less than 750 mm diameter
The pipeline shall be tested in accordance with Appendix O, Paragraph O2.
The pipeline shall be acceptable where the prover passes through the test section showing that the actual short-term deflection is less than that specified in Table 5.6, amended according to Table 6.1, where appropriate.
6.4.3 Pipelines - greater than or equal to 750 mm diameter
The pipeline shall be tested in accordance with Appendix O, Paragraph O3.
The pipeline shall be acceptable where the actual short-term vertical pipe deflection, calculated from Equation O(1), is less than that specified in Table 5.6, amended according to Table 6.1, where appropriate.
SECTION 7 COMMISSIONING
7.1 GENERAL
Acceptance criteria shall be approved by the service owner.
No pipeline shall be placed in service before it has been cleaned of contaminants, before it has satisfied test requirements and, in the case of drinking water pipelines, before the quality of water supplied from the pipeline has met the asset owner’s standards.
Possible contaminants may include—
(a) materials that enter the pipes and fittings during storage and transport;
(b) materials introduced during construction;
(c) bacterial contaminants, which often colonize other contaminants;
(d) infiltration.
7.2 CLEANING WATER SUPPLY PIPELINES
New and repaired water supply pipelines shall be cleaned using the following procedure:
(a) Slowly fill the pipeline;
(b) Clean by;
(i) Swabbing, followed by flushing to completely turn-over the water contained in the pipeline;
(ii) Air scouring (i.e. where compressed air is injected into the water in the main to create unsteady flow conditions during the flushing process);
NOTE: Generally not as effective and usually more difficult than swabbing.
(iii) High velocity flushing (e.g. 2 m/s to 2.5 m/s for 15 minutes).
NOTE: Generally not practical or possible for water mains >DN 300.
7.3 DISINFECTION OF DRINKING WATER SUPPLY PIPELINES
7.3.1 Cleaning
Drinking water supply pipelines, shall be cleaned in accordance with Clause 7.2 and in accordance with any additional requirements of the asset owner.
7.3.2 Disinfection
Drinking water supply pipelines shall be disinfected using the following procedure:
(a) Fill and disinfect;
(b) Flush or neutralise or both;
(c) Refill the main;
(d) Sample for the presence of bacteria;
(e) Certify acceptance; and
(f) Introduce the main into service.