Table 9 of the NEC are having Line-to-Neutral Ohms values. This being used in the Vdrop formula (without root of 3), I will get the Line-To-Neutral Vdrop. Adding the root of 3 to the equation will give me the Vdrop line-to-line.
If I have 1)three phase branch load and 2)single phase branch loads connected line-to-line and 3)single phase loads connected line-neutral,is the calculation of the Vdrop gonna be the following using NEC table 9:
1)3Ph Vdrop = 1.732*L*3Ph current*[R*PF + X*sin(arcosPF)]
2)L-L Vdrop = L*(L-L 1Ph current)*[R*PF + X*sin(arcosPF)]
3)L-N Vdrop = L*(L-N 1Ph current)*[R*PF + X*sin(arcosPF)]
Thanks