NEC 750 KCMIL CABLE, TABLE 310.15(B)(17) / 310.17 VS 310.60(C)(69)

Status
Not open for further replies.

Tuanmetalworks

Mechanical
Mar 12, 2012
1
Hello all,

I am doing a small study on LV and MV cable systems and came across a rather confusing item in the NEC. I am looking at 750 kcmil cables in free air for a 600V system and a 5kV system. To my understanding the ampacity of a 90 degrees cable at 600V is 885 Amps at 30 degrees ambient. But as I look at table 310.60(C)(69) for a 2001-5000 Volts cable, the ampacity is 900 Amps for a MV-90 cable at 40 degree ambient.

So this is where the confusion begins. First off, why would a 2001-5000 V cable have a higher ampacity compared to a 600 V cable? If anything I would expect it to have equal to or less because generally in higher voltage cables there is a copper tape shielding that would also conduct heat due to induced voltage/current. And also don't forget about the 10 degrees increase in ambient.

It would be great if someone can shed some light on this, because I am lost as to why there is an ampacity increase even though the amount of copper to carry the current remains the same.

Please and thank you

 
Replies continue below

Recommended for you

The best and simplest answer is that it doesn't really matter why. You cannot apply logic or the laws of heat transfer to the NEC - you will find it frustrating. It is what it is.

The low voltage table is good up to 2000 V, not 600 V, by the way.

There is a long historical track record for the low voltage conductor ampacities and these very seldom get changed. The low voltage ratings also tend to be more conservative.

The medium-voltage cable construction is somewhat different, and it is conceivable that some of the differences could result in a higher ampacity.

The MV tables were probably submitted to the Code-making panel by cable manufacturers, or NEMA.

I suspect you will not have much luck trying to track down a specific physical reason.
 