Narrow vs wise duct banks
CuriousElectron
194
Hi guys,
From your experience, what determines the layout of the duct bank? If there are multiple conduits being installed in a duct line, say 10 conduits, what drives the decision of 5(row 1)x5(row 2) or 4(row 1)x4(row 2)x2(row 3)?
Thanks,
EE
One factor is entry into manholes. (Person wholes?)
Bill
"Why not the best?"
Jimmy Carter
if this is a high loadfactor environment then conductor heating can be an issue. see Neher-McGrath calculations
There will be a minimum width that will be excavated depending on the typical equipment used. Also the layout impacts the depth required. There will be a minimum depth for the top row. And as Bill says, interface with manholes and handholes is a factor. And ampacity could be an issue.
For a chain type Ditch Witch the minimum width may be less than the size of a single large conduit. Not that I’d suggest a single narrow trench and stacking all of the conduits vertically, just pointing out that minimum width is probably a non-issue.