Am I correct that simply overlaying vectors on transformer nameplates will indicate the phase shift from primary to secondary? Is this true of all transformers nameplates - Dy5, Dy11, Yd1, Yd5, Yd11, etc...?
For example, a Dy1 vector diagram from one of our 115D/13.8Y transformers - if you overlay the wye over the delta it shows the H1 is leading X1 by 30 deg (CCW rotation & A-B-C sequence).
H2 X2
. .
. . .
. . .
. . X1 . . . . . .
. . .
. . .
. . . . . . . . .
H1 H3 X3
On a Dy11 nameplate, the wye would be turned 60 deg CCW (compared to Dy1 vector)?
I appreciate your time answering these kinds of questions.
For example, a Dy1 vector diagram from one of our 115D/13.8Y transformers - if you overlay the wye over the delta it shows the H1 is leading X1 by 30 deg (CCW rotation & A-B-C sequence).
H2 X2
. .
. . .
. . .
. . X1 . . . . . .
. . .
. . .
. . . . . . . . .
H1 H3 X3
On a Dy11 nameplate, the wye would be turned 60 deg CCW (compared to Dy1 vector)?
I appreciate your time answering these kinds of questions.