ThePunisher
Electrical
- Nov 7, 2009
- 384
Hi all,
We have a Siemens Perfect Harmony VFD feeding three motors rated 3 x 4,000 HP, 6.9 kV. The VFD is having isolation transformer with 12.5 MVA primary wye winding and 13 MVA secondary delta winding (18 x windings connected to individual power cells (6 windings per phase).
The VFD pre-charging circuit is protected locally at the VFD by a 250A MCCB whose line side is further fed from a 100A MCCB at the MCC at 600V.
We are aware that the upstream MCC (100A) is under-rated and not matching the VFD local breaker (250A.
However, what bothers us is that the inrush is tripping both or either circuit breakers. With an amplitude of approx. 364Apk-pk or approx. RMS = 128A at approx. 3.5 sec. the 250A VFD MCCB tripped.
There is also case where the 100A circuit breaker at the MCC tripped in approx. 4 secs.
Looking into just the 100A MCCB TCC, it will take a current of approx. 300A to hit the bottom thermal element at 10 secs.
Therefore, it is quite a mystery if either of both breakers trip on a short time while the amplitude is not high enough.
Does anyone had the same experience and if what mitigations were done?
We assume to replace the 100A MCCB with 200A and set both VFD breaker and upsized MCC breaker to an instantaneous settings to override the inrush. Siemens was claiming the high loading on pre-charging will not exceed 60A.
We have a Siemens Perfect Harmony VFD feeding three motors rated 3 x 4,000 HP, 6.9 kV. The VFD is having isolation transformer with 12.5 MVA primary wye winding and 13 MVA secondary delta winding (18 x windings connected to individual power cells (6 windings per phase).
The VFD pre-charging circuit is protected locally at the VFD by a 250A MCCB whose line side is further fed from a 100A MCCB at the MCC at 600V.
We are aware that the upstream MCC (100A) is under-rated and not matching the VFD local breaker (250A.
However, what bothers us is that the inrush is tripping both or either circuit breakers. With an amplitude of approx. 364Apk-pk or approx. RMS = 128A at approx. 3.5 sec. the 250A VFD MCCB tripped.
There is also case where the 100A circuit breaker at the MCC tripped in approx. 4 secs.
Looking into just the 100A MCCB TCC, it will take a current of approx. 300A to hit the bottom thermal element at 10 secs.
Therefore, it is quite a mystery if either of both breakers trip on a short time while the amplitude is not high enough.
Does anyone had the same experience and if what mitigations were done?
We assume to replace the 100A MCCB with 200A and set both VFD breaker and upsized MCC breaker to an instantaneous settings to override the inrush. Siemens was claiming the high loading on pre-charging will not exceed 60A.