I am employed in a Trust and about 10 years ago we moved from a 11kv ring (with 2 11KV REC incomers) and local lv generation at each substation to a 11KV ring with 2 central 1MW 11kv gennnys. We removed the existing 415V gennys bar one which was connected into the substation serving most of our wards and theatre areas. The remaining gennys were removed and replaced with connection boxes allowing mobile gennys to be brought in and connected as required for maintenance/shutdown/breakdowns etc. There was a lot of opposition to this from the Trust engineers at the time believing that we had lost supply security and flexibilty. This genny and the connection boxes have been used many times and proved to be worthwhile modifications.
We have found that staff are still complicated with the old system, we have recently had Tx/breakers trip out resulting in a localised blackout. The staff can not understand why the genny did not start like it used to on the old system. You can not get through that the genny will now only start after 2 REC incomers are lost, and the whole site is black!
We have recently had the original 2 gennys upgraded as well as an additional genny fitted as part of a new PFI build. This work involved downing the site gennys for 6 weeks and replacing them with 2 temp mobile gennys and 1 x 2MVA tx. This was manned 24/7 for 6 weeks, which was easier than the proposal for manning 1 LV genny at each of the substations. 1 benefit of the upgraded controls and new genny is that the site supplies are restored after a power failure/test run within 15 secs now as opposed to approx 45 sec previously worst case. Sounds bad but the depts concerned are used to it now and deal with any issues, you suggest those kind of delays to hospitals that NEVER test thier gennys and they dont know how they could cope. At least our contingencys are tested monthly.
Our gennys have always started together/parallelled to a common bus and then the site feeder breakers have closed systematically to restore supplies in a set order. We then reset load shedded plant. We have experienced start problems and failures on test runs, but this has been control glitches rather than big hit full load problems. Those glitches have been resolved for a long time now.
We have always had Trust HV AP's and I assume with an existing 11KV ring this Trust has their own AP's so this should not be a barrier. I know some Trusts employ the local REC to carry out their switching. LV generation may offer more flexibilty but potentially with a site blackout there is more to fail with numerous gennys.
What about the option of central HV generation, HV distribution, rather than the LV generation, HV transformation, HV distribution. I appreciate there are only a handful of trusts with HV generation/HV distribution but many with HV distribution and LV generation.
Not a technical response I agree but there may be something of interest for you there.
Regards
Sparksski