sberbece
Electrical
- Sep 15, 2003
- 39
Hello !
I would appreciate any opinions on this topic.
Recently I had an argument with one colleague, regarding the grounding of MV generators in a small power plant.
There will be 3 gas generators, 3 MW 13.8 kV, windings start connected.
We agreed that an acceptable technical and cheap solution is to ground each generator’s neutral point through a low impedance earthing resistor, which shall limit the ground fault current of each generator to less than 100 A.
However, I have disagreed when my colleague wants to install a switching device on each generator’s neutral circuit, to be able to open the neutral connection, when the generators are working in parallel, in this way to make sure that at any give time will be always only one generator grounded in the system.
I agree that this solution will limit the power plant single phase to ground fault to maximum 100 A, but on the other hand adds the cost of switching devices and call for troubles during operation of the plant. I believe this switching system couldn’t be justified in this case, when it will reduce the ground fault from 300 A to 100 A, in case of all 3 generators working in parallel.
I believe that the simple solution of directly connecting each generator’s neutral to its earthing resistor will be more appropriated.
The IEEE standards C37.102 clause 3.2.2 – Low resistance grounding and IEEE 142/2007, clause 1.7. and clause 1.7.3 – Paralleled generators in an isolated system, let me understood that directly connected low resistance grounding system is widely use and do not present risk with regards to odd(3rd) harmonic circulation.
Saying these, I would like to know your opinion regarding direct connected low resistance impedance versus low resistance impedance connected through a switch.
Also, what are the advantages of using the switching system for generators grounding?
Thank you in advance for your advice.
I would appreciate any opinions on this topic.
Recently I had an argument with one colleague, regarding the grounding of MV generators in a small power plant.
There will be 3 gas generators, 3 MW 13.8 kV, windings start connected.
We agreed that an acceptable technical and cheap solution is to ground each generator’s neutral point through a low impedance earthing resistor, which shall limit the ground fault current of each generator to less than 100 A.
However, I have disagreed when my colleague wants to install a switching device on each generator’s neutral circuit, to be able to open the neutral connection, when the generators are working in parallel, in this way to make sure that at any give time will be always only one generator grounded in the system.
I agree that this solution will limit the power plant single phase to ground fault to maximum 100 A, but on the other hand adds the cost of switching devices and call for troubles during operation of the plant. I believe this switching system couldn’t be justified in this case, when it will reduce the ground fault from 300 A to 100 A, in case of all 3 generators working in parallel.
I believe that the simple solution of directly connecting each generator’s neutral to its earthing resistor will be more appropriated.
The IEEE standards C37.102 clause 3.2.2 – Low resistance grounding and IEEE 142/2007, clause 1.7. and clause 1.7.3 – Paralleled generators in an isolated system, let me understood that directly connected low resistance grounding system is widely use and do not present risk with regards to odd(3rd) harmonic circulation.
Saying these, I would like to know your opinion regarding direct connected low resistance impedance versus low resistance impedance connected through a switch.
Also, what are the advantages of using the switching system for generators grounding?
Thank you in advance for your advice.