mikeangel
Electrical
- Feb 7, 2008
- 54
Hi!
I need help to sizing the MV cable suitable for the following situation:
I have a 220/60/15kV Power Transformer. The tertiary of the Power Transformer will be connect to a 15/0.4kV (150kVA) Transformer for supplying the Substation Auxiliary Services.
The maximum tertiary power of the Power Transformer is 20MVA. By my calculations the maximum current in the tertiary will be 20MVA/(1.73x 15kVA)=769,8A. The maximum current in primary of the 15/0.4kV (150kVA) Transformer is 5,8A.
In this case what will be the criterion to be applied for the dimensioning of the MV Cable that connects the tertiary of the Power Transformer to the Auxiliary Services Transformer.
Best regards,
I need help to sizing the MV cable suitable for the following situation:
I have a 220/60/15kV Power Transformer. The tertiary of the Power Transformer will be connect to a 15/0.4kV (150kVA) Transformer for supplying the Substation Auxiliary Services.
The maximum tertiary power of the Power Transformer is 20MVA. By my calculations the maximum current in the tertiary will be 20MVA/(1.73x 15kVA)=769,8A. The maximum current in primary of the 15/0.4kV (150kVA) Transformer is 5,8A.
In this case what will be the criterion to be applied for the dimensioning of the MV Cable that connects the tertiary of the Power Transformer to the Auxiliary Services Transformer.
Best regards,