Hi, do you have any experience with the after lying cable sheath testing in case the cable is placed in a protective plastic tube/pipe? I mean the whole lenght. Nice for protection, bad for testing and for fault location. The sheath has no direct contact to the ground so you can not guarantee the sheath is fault free. Any experiences/tips?
I have one negative experience - we did the sheath test on a new MV XLPE cable some way (sometimes it is possible even with the tubes)- Result ok as well as the other acceptance tests(VLF 3Uo 60min+PD testing). After 1 or 2 years in operation the fault occured. The problem was in a cable insulation but the manufacturer asked for the after lying test results, and of course, they were claiming it could be a mounting/laying problem. The service company said the test were OK so it could not be mounting/laying problem. The manufacturer replied: "how did you make a sheath test in case it was placed in in a protective plastic tube/pipe? It is almost impossible". (what I agree too). It was very difficult to find out what was the problem - the cable was still under warranty and we were asking for the compensation.
I have one negative experience - we did the sheath test on a new MV XLPE cable some way (sometimes it is possible even with the tubes)- Result ok as well as the other acceptance tests(VLF 3Uo 60min+PD testing). After 1 or 2 years in operation the fault occured. The problem was in a cable insulation but the manufacturer asked for the after lying test results, and of course, they were claiming it could be a mounting/laying problem. The service company said the test were OK so it could not be mounting/laying problem. The manufacturer replied: "how did you make a sheath test in case it was placed in in a protective plastic tube/pipe? It is almost impossible". (what I agree too). It was very difficult to find out what was the problem - the cable was still under warranty and we were asking for the compensation.