We have a 11 kV bus bar with about 14 MVA of loads (90% motors).
We got (customer data) the short circuit current values: 35 kA as Ikss (subtrans I)
I feel such value a bit too high. Also considering the motor contribution I was expecting 12-13 kA.
(assuming a 15 MVA 9% trafo feeding the system we get 8.75 kA at 11 kA + about 3600A as motor contribution (sum of their starting currents))
What's your experience?
I have the impression that we could get 35 KA only if directly connected to a bus with the generators (we don't know how "our" 11Kv bus is connected)
Thanks in advance for any feedback
 
I think that 35kA (for 1s or 3s) is the rated short-time withstand current of the switchgear

Alex68
 
Thanks for the answer but the bus rated current is 40 kA for 3sec.
The value we got is 35.2 kA, it's coming from a calculation.
35.2 looks like the Ip (peak value)....
 

Hi AMBMI
If your 11 kV distribution bus should be supplied from a 40 MVA 7.5%uk 33/12 kV Transformer from an Utility Substation the total Ikss would be 35 kA as per your customer data. The shortcircuit current depend on grid impedance more than on your facility motors.
I don't think there is a utility transformer dedicated for your supply only.
If we take:
All motor Ist/In=7.5
14 MW 100% motors
Substation transf.40 MVA 7.5% uk
50 Hz only
Medium Voltage [Substation]=33 kV
Inom33kV= 50 KA [33 kV Utility Grid ]
No feeder [12 kv supply to your Facility] impedance [Distance =0 ]
we will get Ikss=35 kA
Best regards

 