I'd like to hear Shophound's experience with RH sensors too.
In museums, they need to be very unobtrusive if not completely hidden. Often, that leads to a flush-mount installation that can really mess with both sampling and accuracy.
A recent project I had to analyze had humidity transmitters installed flush, with only the sensing element sticking out front of a wall plate a few millimeters. The electrical box in which they were mounted was surrounded on all sides by insulation.
What a lot of folks don't take into account is that a 4-20 mA transmitter dissipates an appreciable amount of power. The most common sensors do 4-20 mA over 0-100 %RH and are powered with 24 VDC supply. So at 50% RH (12 mA), if the controller has a 250Ω input impedance, the voltage drop across the transmitter electronics must be 24 - (0.012 x 250) or 21 VDC. So the transmitter is dissipating 21V x 0.012A or 0.25W. That's a lot of heat inside a 2" x 2" x 4" insulated box. Temperature rise in the box was measured at 6° to 8°F, and was enough to offset the RH sensing element's own temprature sensor by about half that amount. With an elevated (false) temperature measurement, the sensor reports an artificially lower (inaccurate) RH.
Our solution was to separate the loop electronics from the sensor, put them in separate boxes with insulation between. Worked much better.
This probably happens often but is not often noticed, in my opinion. The only reason it came to light for me to study was the particular museum project. It had temporary loan of some Egyptian antiquities, and the Egyptian authorities came periodically to measure temperature and humidity around their treasures. They had very expensive, tightly calibrated instruments that showed the error in the wall sensor measurements.
We had other issues with air circulation to the sensors since they were so tight against the walls as well, but the museum staff came up with a number of creative and very effective solutions for those too.
I decided to throw all this in here to see if anyone else ever ran into such? Self-heating of humidity transmitters doesn't get a lot of discussion...
Good on ya,
Goober Dave