Hello, I am new to this site and really found it to be informative so far. I have a question regarding multistory wood shear walls and uplilft.
Two methods for determining overturning and uplift are described below for a two story building. Dead loads are neglected for the description.
Method 1) Loads at roof and floor levels are multiplied by the respective height above ground (x=floor to floor height) and divided by the wall length to determine overturning.
Uplift = [Roof*(2x) + Floor*(x)]/L
Method 2) Story shears are used at each level to determine uplift at each level. Second floor uplift = (Roof*x)/L and uplift at first floor = [(Floor+Roof)*x]/L. If uplift occurs at the second floor this force is added to the first floor reaction to determine what hold down, if any, is required at the foundation.
Design of Wood Structures by Breyer says to examine the stability of the individual shear walls. If the individual parts are stable, the entire building is stable. It goes on to say that overturning of the entire building (such as steel rigid frames) is not done for a wood shearwall building.
Would you interpret this to mean you would use method 2 described above for wood framed buildings or still use method 1? What approach do other people use to determine hold downs and uplift forces at wood shear walls? I have found one example on the internet by Philip Line of a two story shear wall. There is not a large amount of information out there for multistory wind shear walls.
Please let me know what you think and if you would like any clarifications. Sorry for being longwinded.
Thank you.
Two methods for determining overturning and uplift are described below for a two story building. Dead loads are neglected for the description.
Method 1) Loads at roof and floor levels are multiplied by the respective height above ground (x=floor to floor height) and divided by the wall length to determine overturning.
Uplift = [Roof*(2x) + Floor*(x)]/L
Method 2) Story shears are used at each level to determine uplift at each level. Second floor uplift = (Roof*x)/L and uplift at first floor = [(Floor+Roof)*x]/L. If uplift occurs at the second floor this force is added to the first floor reaction to determine what hold down, if any, is required at the foundation.
Design of Wood Structures by Breyer says to examine the stability of the individual shear walls. If the individual parts are stable, the entire building is stable. It goes on to say that overturning of the entire building (such as steel rigid frames) is not done for a wood shearwall building.
Would you interpret this to mean you would use method 2 described above for wood framed buildings or still use method 1? What approach do other people use to determine hold downs and uplift forces at wood shear walls? I have found one example on the internet by Philip Line of a two story shear wall. There is not a large amount of information out there for multistory wind shear walls.
Please let me know what you think and if you would like any clarifications. Sorry for being longwinded.
Thank you.