The application consists of four 1/2HP 115V 1[Φ] In / 230V 3[Φ] Out VFD's powering 1/2HP gearmotors that drive simple conveyors. The conveyors are dual narrow urethane V-belts riding on steel guides carrying egg flats. The VFD's will be loaded at approximately 75%. The machine has ground fault protection for personnel (Class A device) due to machine operation in a washdown environment. Also, the machine requires CE rating and therefore has an EMI/RFI filter on the incoming line. The drives are tripping the GFCI. An Isolation Transformer is being proposed to prevent the GFCI from tripping.
Common mode chokes on the motor leads are being proposed in lieu of shielded cable. A toroidal ferrite core has been applied (5 turns) to the PE (ground) conductor feeding the VFD enclosure. The GFCI is upstream of the VFD cabinet at the power feed to the machine. The drives manufacturer representative recommended increasing the carrier frequency in an attempt to minimize the leakage current.
1) What are the design considerations when applying multiple VFD's on one isolation transformer?
2) Should the transformer be K rated and/or shielded?
3) What are the design considerations when applying VFD's with a GFCI?
4) Is it practical to utilize VFD's and GFCI's, or in other words, is there any hope of preventing the GFCI from tripping?
5) Any other comments on the application?
Thanks everyone for your time.
Amp
The application consists of four 1/2HP 115V 1[Φ] In / 230V 3[Φ] Out VFD's powering 1/2HP gearmotors that drive simple conveyors. The conveyors are dual narrow urethane V-belts riding on steel guides carrying egg flats. The VFD's will be loaded at approximately 75%. The machine has ground fault protection for personnel (Class A device) due to machine operation in a washdown environment. Also, the machine requires CE rating and therefore has an EMI/RFI filter on the incoming line. The drives are tripping the GFCI. An Isolation Transformer is being proposed to prevent the GFCI from tripping.
Common mode chokes on the motor leads are being proposed in lieu of shielded cable. A toroidal ferrite core has been applied (5 turns) to the PE (ground) conductor feeding the VFD enclosure. The GFCI is upstream of the VFD cabinet at the power feed to the machine. The drives manufacturer representative recommended increasing the carrier frequency in an attempt to minimize the leakage current.
1) What are the design considerations when applying multiple VFD's on one isolation transformer?
2) Should the transformer be K rated and/or shielded?
3) What are the design considerations when applying VFD's with a GFCI?
4) Is it practical to utilize VFD's and GFCI's, or in other words, is there any hope of preventing the GFCI from tripping?
5) Any other comments on the application?
Thanks everyone for your time.
Amp