Back to the original question -
The concern with generators operating in parallel on a common bus is with third harmonic current circulating through the common neutrals. There are several approaches to avoiding this problem, some of which are -
- Provide each generator with a neutral disconnect switch (NOT a circuit breaker). Only one disconnect is closed at any one time, so that there is no posssibility of circulating current.
- Provide each generator with an individual neutral grounding resistor; the resistors have to be sized to carry the expected level of circulating third harmonic current. This approach has the disadvantage that the ground fault level is variable, depending on the number of generators on line.
- Install a separate grounding transformer with a neutral grounding resistor (this can be a wye/delta station service transformer or a zigzag grounding transformer). None of the generators are grounded in this case, all generator neutrals operate isolated.
In all of the above, sensitive and selective ground fault relaying is of paramount importance. There is a need to minimize the ground fault current, so as to minimize stator iron burning for generator ground faults, while still providing a high enough current for selective tripping.
One relaying approach that works well with the separate grounding trasformer approach is to install directional ground relays on each generator circuit, with time delayed overcurrent protection on the grounding transformer itself.
On balance, I believe that the separate grounding transformer is perhaps the best solution for a new installation, where there is a transformer isolating the generation from the distribution system. I have worked recently with a utility 11.5 kV system, connecting 4x10MW generators to a common bus, which uses this method of grounding. No problems to date, and no circulating currents. Am also presently working on an industrial system which has individual NGRs, and am wrestling with setting relays for the range of ground fault current available.
One other point re the above responses - under no circumstances should there be a circuit breaker in the neutral circuit which will trip under fault conditions. The faulted generator itself and its associated main breaker would be tripped for the ground fault condition.
If a disconnect switch is provided in the neutral circuit, it can be a manually operated metal-enclosed switchgear device or an open switch, depending on the type of construction in the station. I have seen older stations with the neutral busbar and individual switches mounted on the wall in a switchgear room, but I wouldn't recommend this for modern practice.
Another useful reference, if you have access to a copy, is the old Westinghouse Electrical T&D Reference Book - see chapter 19. Hope this helps to clarify the issue.