Well Travis, since you asked:
I agree with your interpretation. The last mega warehouse/manufacturing/Group H occupancy I reviewed and approved was a 764,000 square foot bottled water plant (largest in North America). We installed a master Fire Department Connection downstream of the pump suction. The FDC had its own 100 foot feed main and was located near a municipal hydrant. Frankly, these demands are starting to get so big with the new sprinkler technology I am really scrutinizing pipe sizes for remote FDCs.
While our designs are different, your going to be in the same condition if the pump takes a dump. That is why an accessible, easily identified FDC is so important.
I believe NFPA 13 gives us the flexibility to allow both designs. My question is "what is the other option?" In your case Travis, 33 different FDCs sure as hell will confuse the responders and then that is when the poo hits the fan. Firefighters must understand (especially in warehouses protected by the new sprinkler technology) that they need to start pumping the FDCs as their first fireground action, not their third. Second action: send a firefighter to the pump (when one is provided) to make sure it is running.