Hello msjls2,
First to do is Check the leads labeling, if your motor is manufactured in U.S the leads are labelled with numbers from 1 to 6. If this is the case Then disconnect the motor from the Wye-Delta starter and connect the motor for D.O.L : L1 to 1-6, L2 to 2-4 and L3 to 3-5.Earth to Motor´s frame.
If the motor is manufactured by IEC Standards then the leads are labelled like U1,V1,W1,U2,V2 and W2 for D.O.L start: L1 to U1-W2, L2 to V1-U2 and L3 to W1-V2.Earth to motor´s frame.
Regards.
Petronila