SAMBOY
Electrical
- Mar 5, 2003
- 12
We have a 2.2MW, 11kV, 60Hz Motor for a Compressor.
During start-up at no load (uncoupled)the starting current is 251A then the voltage drops from 11kV to 8.66kV.
What is the effect of the voltage drop to the motor? What are the possible solutions or your recommendations if these will affect the motor?
(Just an added information, The motor is being supplied by a 3.5MVA 13.8kV/11kV Delta-Wye Connected transformer, 4.75 impedance)
We tried to measure the primary voltage of the transformer during start-up and its voltage drops from 13.8kV to 12.3kV.
During start-up at no load (uncoupled)the starting current is 251A then the voltage drops from 11kV to 8.66kV.
What is the effect of the voltage drop to the motor? What are the possible solutions or your recommendations if these will affect the motor?
(Just an added information, The motor is being supplied by a 3.5MVA 13.8kV/11kV Delta-Wye Connected transformer, 4.75 impedance)
We tried to measure the primary voltage of the transformer during start-up and its voltage drops from 13.8kV to 12.3kV.