X49
Electrical
- Apr 30, 2009
- 106
I am adding a 30hp, 240V centrifugal pump load to a 150kW gas genset. The pumphouse will be at the end of a 1000ft 480V feeder, and also has some small lighting and heating loads. A 75kVA transformer will step the voltage down from 480V to 240V (3 phase).
I'm concerned that the voltage dip may be excessive when the pump starts due to the genset voltage dip, feeder voltage drop, and the voltage drop across the transformer winding.
Calculating the voltage dip based on rated motor inrush current, I get a dip of 31%. If I iterate my calculations to account for reduced current due to voltage dip, I get a dip of 23.5%. (12% genset dip, 5% cable and 6.5% transformer).
Is this an acceptable level of momentary voltage dip for the pump, motor contactor, and lighting loads? I could increase the size of cable and/or transformer to compensate but the costs will add up quick, and it may not be worth it just to prevent lighting flicker. Total steady-state voltage drop is well under 5%.
I'm concerned that the voltage dip may be excessive when the pump starts due to the genset voltage dip, feeder voltage drop, and the voltage drop across the transformer winding.
Calculating the voltage dip based on rated motor inrush current, I get a dip of 31%. If I iterate my calculations to account for reduced current due to voltage dip, I get a dip of 23.5%. (12% genset dip, 5% cable and 6.5% transformer).
Is this an acceptable level of momentary voltage dip for the pump, motor contactor, and lighting loads? I could increase the size of cable and/or transformer to compensate but the costs will add up quick, and it may not be worth it just to prevent lighting flicker. Total steady-state voltage drop is well under 5%.