Hello CJCPE
The current curve should drop fairly smoothly from LRA at zero speed through FLA at rated speed to NLA at synchronous speed
I do not agree with this. This suggests a straight line with reducing current when in reality, the curve is much closer to square. There will be a small drop off in current from zero speed to greater than 50% speed, but this drop off may only amount to 10% of LRA, so at 50% speed you could easily have over 90% of LRA. The current generally only begins to fall significantly around 80-85% of full speed so at 80% speed, you could easily have 75% of LRA or higher.
The shape of the current speed curve is very rotor design dependant, but two pole motors are very square. Higher power and higher efficiency motors tend towards a squarer curve.
For example, I have jsut looked up a Toshiba 90KW 4 pole motor and I find that the LRA is 990 amps, and at 80% speed, the current is 840Amps. The full load current is 164 Amps.
A WEG 2 pole 55KW motor (400V 50Hz) has a LRC (LRA) of 850%. at 50% speed, the current is 825% and at 80% speed the current is 670%.
Hello nhee
In comparing a motor torque vs speed curve vs a driven load (pump) torque vs. speed curve, the motor torque drops below load torque at about 80% of rated RPM. My understanding of the real-world result would be that the pump would start, accelerate to 80% rpm, and then hold that speed, drawing Locked Rotor Amps, until the motor protective devices tripped. Is this correct?
Yes, if the load torque curve crosses the motor torque curve, the motor can not accelerate any further and so it will remain operating at that speed until either you step to full voltage (if you are using a reduced voltage starter) or the protection operates, or the smoke comes out.
The current drawn at 80% speed will be less than LRC (LRA) but will typically be in the order of 50 - 80% of LRA, so significantly higher than the rated current (300% - 600%)
Best regards,
Mark Empson