nightfox1925
Electrical
- Apr 3, 2006
- 567
We have one 13.8kV double ended switchgear with NO bus tie with two outgoing feeders feeding two 4.16kV MCCs via two 13.8-4.16kV step down transformers in each bus (total=4 MCCs). These MCCs supplies power to several 4kV induction motors. There are 5 nos 4kV motors in each MCCs which have time delayed auto-restart control scheme. Based from load flow and motor starting, it is proposed to group these motors with auto-restart into two (Group A and Group B). In the event of an open transition transfer scheme, group A motors will auto-re-start, run up to full load speed and then group B will automatically restart.
The existing auto restart control on each motor starter consists of two timers: ON-Delay TD2 which is set at 0.6 sec used to start the contactor and wired to bypass the seal-in contact. The OFF-Delay timer TD1 acts to delay breaking the continuity of the auto-start contact of TD1. During a temporary outage of control supply, TD1 opening is delayed by 6 seconds, if control power has returned within 6 seconds, ON-delay TD1 coil is energized and its contact closes within 0.6 seconds and energizes the main contactor via TD2 permissive contact. If control power resumption exceeds 6 seconds, the OFF-delay timer TD1 breaks and the auto-restart function is blocked.
It is proposed that the Group A motors existing timer settings will be retained. However, for group B motors, a 10 second additional timing should be added to both TD1 and TD2 to ensure that the highest rated motor in Group A has successfully reached full load speed. All motors are rated for auto-restart duty.
Are there any concerns or recommendations? We appreciate any valuable comments. Thank you.
The existing auto restart control on each motor starter consists of two timers: ON-Delay TD2 which is set at 0.6 sec used to start the contactor and wired to bypass the seal-in contact. The OFF-Delay timer TD1 acts to delay breaking the continuity of the auto-start contact of TD1. During a temporary outage of control supply, TD1 opening is delayed by 6 seconds, if control power has returned within 6 seconds, ON-delay TD1 coil is energized and its contact closes within 0.6 seconds and energizes the main contactor via TD2 permissive contact. If control power resumption exceeds 6 seconds, the OFF-delay timer TD1 breaks and the auto-restart function is blocked.

It is proposed that the Group A motors existing timer settings will be retained. However, for group B motors, a 10 second additional timing should be added to both TD1 and TD2 to ensure that the highest rated motor in Group A has successfully reached full load speed. All motors are rated for auto-restart duty.
Are there any concerns or recommendations? We appreciate any valuable comments. Thank you.