We are installed three motors with 650A FLA @ 460V, each motor is to be controlled by a VFD within motor vicinity, and there are two old 3p/1600A fusible switches available on the distribution switchboard, neither switch is equipped with GF protection.
I am thinking of two options, one is to connection 2 of 3 motors to one of the 3p/1600A switchs, and then have same-size tap conductors wired to each motor. As per NEC, the conductor for a group motor can be sized at 125% of the largest motor plus 100% of the remainder (1.25*650+650=1462.5A @ 460V), and connect the 3rd motor to the other 3P/1600A switch. If we go with this option, we will have to retrofit both switches with GF protection sensor and trip mechanism. The the option is to replace the existing switches with (3) new insulated power breakers, one for each motor.
My questions is: As per 2005 NEC 430.110(A), the disconnect for motors can be sized at 115% of the NEC FLA table value (table 430.247-430.250) , however the overcurrent protection for the motor circuit have to be 125% of the NEC FLA table value. Another words, the fuses or circuit breaker would be bigger than the switch. Is my interpretation of the NEC correct?
If 115% is ok, we will not have to install 1000A power breakers, 800A will be adequate, do we still have to provide GF protection? since they're not 1000A or move @ 460V. Much Thanks.