First of all I agree with Scotty. However, here are my thoughts
![[ponder] [ponder] [ponder]](/data/assets/smilies/ponder.gif)
.
In my opinion [better speaking :"my feeling is"], a 5 MW induction motor and 6.6 kV ratings has to be 3000 rpm[2 poles 50 Hz] .
In this case the moment of inertia has to be 100-150 kg.m^2.Let’s take the total moment of inertia [motor and the load] as 1500 kg.m^2.
In my opinion, if no-load torque is involved the motor velocity reaches the top in 1-2 seconds.
Let's say the starting torque could be arranged-if we choose the right rotor resistances-from 0.8 to
1.2 and an average of 1 of rated torque, if the stator is supplied with rated voltage[6.6 kV].
In my opinion also, a transformer of 2 MVA short-circuit voltage could be 6-8% and the utility short-circuit apparent power could be 250-500 MVA.
If the x/r =5 for both [transformer and system 22 kV] then total X=1.88 to 1.37 ohm and R=0.38 to 0.27 ohm[at 6.6 side].
DV=sqrt(3)*Imot*(R*cos(fi)+X*sin(fi))
The problem is the power factor. The exterior resistance will increase the power factor initially[0.9?]
as it is the large resistance inserted-even the rotor reactance is elevated too-and will be close to 0.2[?] at the start of last stage.
In this case the voltage drop will be 17-22% at the beginning and will be 30-35% at the final stage.
I think it is a chance to succeed the start.
If the no-load motor current will be not more than 30% the transformer could manage this for a while.