My recommendation for motor starting includes:
a. - Load speed-torque curve and reflected constant of inertia at the motor shaft.
b. - Motor speed- torque curve, speed-current curve and motor current-time thermal withstand.
c. - Type of start configuration. (Reduced voltage, part-winding, wye-delta, soft starter, etc).
d. - Load conditions; (uncoupled, reduced load, etc).
e. - Power supply parameters and voltage drop due to current demand at motor start.
f. - Calculation of motor starting time. Based on the speed- torque curves, system inertia and voltage-frequency applied.
g. - Analysis of the line and motor heating and current relays coordination based on starting time, motor current and heating curves.
h. - Verify allowed number of starts.