Samy81: Yes - within the constraints of factors which affect impedance, the "basic" short cut formulae can achieve fairly realistic approximations for certain changes. As you have already noted, the relationship between starting (inrush) current and applied line voltage is more-or-less linear, at least when you talk about per unit values. What this really means is that when rated (1.0 pu) volts is applied, the inrush current is also 1.0 pu. If a lesser voltage such as 0.8 pu is applied, then the starting current will be likewise reduced to 0.8 pu.
Furthermore, the relationship between applied voltage and starting torque is a square law. This means that a 1.0 pu voltage will result in the machine developing 1.0 pu starting torque (and thus accelerating torque). At reduced voltage - like 0.8 pu - the developed torque is 0.8 * 0.8 = 0.64 pu of the RATED starting (and accelerating) torque. This is why having too much line drop (or too little transformer) between the utility and the machine can cause the motor to be unable to accelerate the driven load.
In essence, the correct machine model is indeed a "constant impedance" approach, rather than a "constant kva" approach.