The cause of high starting current: <br>
The starting current will be high (of the order of 4 to 6 times of rated current, depending on the motor rating) if it's on no-load or on load. The current will come down as the motor picks up speed, and settles down at a stable state. When the motor is ON-LOAD, because of the higher inertia more time is needed to attain this state. After that, a steady current will be drawn- the current will be more if the load is more.<br>
<br>
Usually, the no-load current will be 2-10% of the full load current- again, this will depend on the motor-rating.<br>
<br>
I've one suggestion to make in Merbas's posting above:<br>
<br>
Usually, for heavy loads, we use the STAR-DELTA transformation, and not delta-star. If you've three windings A1-A2, B1-B2 and C1-C2 where '1' indicates start of winding and '2' indicates the end,<br>
for Star connection, you connect A2-B2-C2 together. The 3-phase power is applied across A1, B1 andd C1. This will cause less current to flow through the windings.<br>
Once you pick up speed, you quickly change over from star to delta.<br>
<br>
For delta, you connect A2-B1 together, B2-C1 together and C2-A1 together. The 3-phase supply is connected across the three junctions. This allows more current with the same 3-phase voltage.<br>
<br>
Regards.