Phase to Phase. We are feeding the motor starter with a contactor that is approx. 1000 ft. Note the feed contactor stay energized all the time. The caps for the motor come directly off the motor stater (vac bottles) and the motor feeder is approx. 50 foot long. The waveforms are of a motor start. We are using a Dranetz to capture this wave.
On a side note the reason we are looking at this is on occasion, probably 2 time a year we loose other 4160 volt motors that are on the same buss. We orginally thought we had a voltage sag problem, but after monitoring the system we found nothing. We did a motor staring simulation with E-tap to see what a locked rotor would do the voltage and even in this case the voltage drop would not be enough to cause any problems. We had our motor rebuild shop come in and test motor, we have tested the cables, contactors, multilin and every thisng else we coudl think of. The only strange event we have captured is 12-16-2008, the jagged edges on the ringing.