We have a system that's running close to the feeder XFMR's Full-load MVA rating:
LOAD-FLOW MVA: 16.0543
XFMR Full-LD MVA: 16.625
When a large motor starts, the starting current increases the load to about 21.2914 MVA which is about 28% more than the rated value of the XFMR, but of course that only lasts for few cycles. My question is, does that hurt the XFMR in any way?