agreed.
Although the f in the numerator has not been clearly defined.
I would prefer to say sync speed = 2*FL / poles
where FL is line frequency.
Put the units in and you'll see the need for any additional required unit conversions such as 60rpm / hz.
Actual speed for general purpose NEMA design B motor is required to be in the range 0-5% below sync speed, and usually in the range 0-1% below sync speed.